Power Problem, suggest me please...
My PC Specifications are
LG FLATRON E700SH
Intel Desktop Board D865GVHZ
2 x 512 MB RAM
Lite-ON DVD RW SHW-1635S
Segate SATA 250 GB Hard Disk
I have connected my PC to Proview's 600VA UPS.
But when Lights are gone, my PC gets turned off directly in a sec. then tries to turns on again automatically, but the UPS does not get the load of my PC and starts beeping faster immediately.
Also, If I start my whole PC and select "Degauss" the whole Power supply from the UPS is cut off & the UPS makes a large beep. I even charge the ups fully.
I've even tried Proview's 700 VA UPS but it does not work.
What should I do? Should I change the UPS or the Monitor???
|
|
|
|
Advertisements. Register and be a member of the community to get rid of them.
|
|
Advertisement
|
|
24-08-2007, 11:01 PM
|
#2 (permalink)
|
|
ToTheBeatOfUrHeart
Join Date: Feb 2006
Location: Boston,Newyork
Posts: 1,882
|
Re: Power Problem, suggest me please...
Change the UPS brand,go for APC or power safe.
__________________
Mobo - P5N32-E SLI,P5N-E SLI|GFX - 2x8800GTS,8800GT|Processor - E6550,E6600|PSU - CM EP 600,HX620W|Physics - 2x8600GT
|
|
|
25-08-2007, 12:13 AM
|
#3 (permalink)
|
|
Alpha Geek
Join Date: Aug 2004
Location: Ahmedabad, Gujarat
Posts: 896
|
Re: Power Problem, suggest me please...
probably the battery in the UPS is faulty.........
one other problem might be that the response time of the UPS might be higher....but 99.9 percent chance that this one is not the problem.....
if u think the monitor is creating problem then remove the monitor cable from the UPS and see...
|
|
|
25-08-2007, 01:01 AM
|
#4 (permalink)
|
|
Banned
Join Date: May 2004
Location: Baudland
Posts: 2,433
|
Re: Power Problem, suggest me please...
r u sure ur UPS has been mfg by proview
AFAIK dey not in UPS business
dey basically in Display devices
appears like ur BATTERY has gone kaput
u mite wan 2 get it replaced/serviced from d authorised service center
Quote:
|
Originally Posted by moshel
remove the monitor cable from the UPS and see...
|
  
of wat GOD-forsaken use is a UPS if it is not connected 2 d monitor
light chali gayi toh CPU a kya achaar dalega ya aarti utarega
|
|
|
25-08-2007, 04:02 PM
|
#5 (permalink)
|
|
Right Off the Assembly Line
Join Date: Aug 2006
Posts: 7
|
Maine Monitor ka aachar daal ke dekha.
I connected only the Cabinet then turned on the UPS, quickly started pressing the delete button, so that windows does not start. 
After turning off the main Power Supply, PC did not get turned off and the beeps of the UPS were not much faster as before.
I don't think there is any problem with my battery, only the monitor is heavy.
So, now if I want to change the monitor, should I go for the LCDs???8)
Tell me some models, please.
I want to make sure that, now if I change the monitor, there should not be any problem.
|
|
|
25-08-2007, 04:08 PM
|
#6 (permalink)
|
|
Banned
Join Date: May 2004
Location: Baudland
Posts: 2,433
|
Re: Power Problem, suggest me please...
APCs 500VA UPS
will even support a 19" CRT without complaining
|
|
|
25-08-2007, 04:25 PM
|
#7 (permalink)
|
|
In The Zone
Join Date: Apr 2006
Posts: 371
|
Re: Power Problem, suggest me please...
^^^^  500Va Cannot Take a 19 CRT for Sure
|
|
|
25-08-2007, 04:29 PM
|
#8 (permalink)
|
|
Banned
Join Date: May 2004
Location: Baudland
Posts: 2,433
|
Re: Power Problem, suggest me please...
Quote:
|
Originally Posted by vinyas
^^^^  500Va Cannot Take a 19 CRT for Sure 
|
of course it duz
APCs 500VA UPS provided a back-up of 10 mins -printer -scanner
i no this 4 sure cause d comp in our colege's teacher's room has got it
check out d packaging of d UPS it is clearly mntioned there
|
|
|
25-08-2007, 04:33 PM
|
#9 (permalink)
|
|
Norms Buster
Join Date: Feb 2007
Location: Bangy
Posts: 317
|
Re: Power Problem, suggest me please...
Quote:
|
Originally Posted by vinyas
^^^^  500Va Cannot Take a 19 CRT for Sure 
|
I strongly agree with him. If the monitor is a TFT then it may work, but not a 19" CRT !!!
|
|
|
25-08-2007, 04:37 PM
|
#10 (permalink)
|
|
Banned
Join Date: May 2004
Location: Baudland
Posts: 2,433
|
Re: Power Problem, suggest me please...
d00d do u have first hand exp??
or just commenting on d basis of sum heresay dat was quoted 2 u by ur nanny during ur bedtime nap
i've used d comp myself in d teacher's room and have cghecked it out 4 myself
i disconnected d pwer 4 7 mins b4 restoring it back and not 1s did it complains (only beeped  )
|
|
|
25-08-2007, 04:38 PM
|
#11 (permalink)
|
|
The Devil
Join Date: Feb 2006
Location: 0x02AE88C6FF
Posts: 983
|
Re: Power Problem, suggest me please...
I too faced the same problem. So I got myself an 800VA double battery Microtek UPS. No problems now.
|
|
|
25-08-2007, 04:43 PM
|
#12 (permalink)
|
|
Banned
Join Date: May 2004
Location: Baudland
Posts: 2,433
|
Re: Power Problem, suggest me please...
i m not d only 1 who knows dat APC 500VA supports 19"CRT
Quote:
Why I purchased it
This unit was purchased to replace my APC Back-UPS 200, only because I needed more voltage for a Pentium IV computer and 19-inch monitor. The reason I purchased APC again is because I’ve been very pleased with their other products. APC has become the industry standard in uninterruptible power supplies (UPS). I’ve worked with several state-of-the-art computer facilities that use nothing but APC and they report only minimal problems with their units. Although I primarily purchased this unit for major surge protection and backup power, I also purchased it because I’m concerned about the frequent minor power spikes and sags that can damage electronics over time. This unit absorbs these spikes (and other line noise) and keeps the power level up where it should be.
|
SOURCE
i hope 1 is enuf 4 u
if u want more such testimoinals search 4 it urself
|
|
|
25-08-2007, 04:52 PM
|
#13 (permalink)
|
|
In The Zone
Join Date: Apr 2006
Posts: 371
|
Re: Power Problem, suggest me please...
 Mate thats a APC Back-UPS Office 500VA (BF500) which is way More Expensive The Normal APC BACK-UPS 500VA(BR500) which we usually Buy for Home Use
Two Different Models ,Two Different Stories
|
|
|
25-08-2007, 04:53 PM
|
#14 (permalink)
|
|
Banned
Join Date: Oct 2006
Location: Durgapur
Posts: 1,785
|
Re: Power Problem, suggest me please...
APC 500VA is a gr8 ups.it handles my rig w/o any probs.Cud be a earthing prob.get it checked.
|
|
|
25-08-2007, 04:55 PM
|
#15 (permalink)
|
|
Banned
Join Date: May 2004
Location: Baudland
Posts: 2,433
|
Re: Power Problem, suggest me please...
Quote:
|
Originally Posted by assasin
APC 500VA is a gr8 ups.it handles my rig w/o any probs.Cud be a earthing prob.get it checked.
|
  no body here has started usin 1, other [dan me and u] 
tryin 2 tell sum ignorant sould wat 500VA stands 4
|
|
|
25-08-2007, 05:04 PM
|
#16 (permalink)
|
|
Banned
Join Date: Oct 2006
Location: Durgapur
Posts: 1,785
|
Re: Power Problem, suggest me please...
^^^ if they dont believe then they sud try 1 themselves.
|
|
|
25-08-2007, 05:14 PM
|
#17 (permalink)
|
|
Banned
Join Date: May 2004
Location: Baudland
Posts: 2,433
|
Re: Power Problem, suggest me please...
Quote:
|
Originally Posted by vinyas
 Mate thats a APC Back-UPS Office 500VA (BF500) which is way More Expensive The Normal APC BACK-UPS 500VA(BR500) which we usually Buy for Home Use
Two Different Models ,Two Different Stories 
|
d00d wen d POWER RATIN has been mentioned den price has got nothin....i repeat....absolutely nothin 2 do with d max O/P power
u may buy a 1000$ 500VA UPS or a 60$ 500VA UPS
both will give u a maximum O/P power of 500 Watts
just bcos u shelled out 1000$ 4 d 500VA UPS does not mean dat it will support a datacenter
d only difference between d two, besides features, is d quality of sine wave
if APC brings out 2 models of 500VA and prices it differently, it is only bcos d more exp 1 has better features and NOT HIGHER POWER RATING
nad since both d models r fom APC, dey both gonna have d same sine wave pattern
TIME 2 CHANGE UR BED-TIME NANNY D00D
|
|
|
25-08-2007, 05:45 PM
|
#18 (permalink)
|
|
Wise Old Owl
Join Date: Mar 2005
Location: shhhh!!!!! on a sniper point
Posts: 4,200
|
Re: Power Problem, suggest me please...
the latter will be online UPS. They costa more
My Hykon 600VA cannot bear 17" flat CRT [power consumption is bout 80w~90w].
A 19" flat CRT wun consume as much as 110~120w. For an 500VA UPS to take that load, the system load shud be very low, that is no gcard, 1 HD, 1 CD, etc.
__________________
G1: PII X4 B50 4.0 | TRUE 120*2 | TA790GXB A2+ | 4GB DDR2 GSkill 1200 | Audigy 2 | HD4870 | HEC 550 | MX 518.
G2: AII 240 | M2N 68AM+ | 3GB| 8800GT | Zebby Plat 500
G3: XPS M1530 |
FZ 16.
|
|
|
25-08-2007, 05:56 PM
|
#19 (permalink)
|
|
Right Off the Assembly Line
Join Date: Aug 2006
Posts: 7
|
I am thinking to go for APC.
|
|
|
25-08-2007, 06:04 PM
|
#20 (permalink)
|
|
Banned
Join Date: May 2004
Location: Baudland
Posts: 2,433
|
Re: Power Problem, suggest me please...
Quote:
|
Originally Posted by aravind_n20
For an 500VA UPS to take that load, the system load shud be very low, that is no gcard, 1 HD, 1 CD, etc.
|
along with 19"CRT,
it can take d required load with a GPU also
as 4 ur 600VA not supportin a 17" CRT, monitor der must b sumthin wron with ur UPS
maybe d true power rating was not revealed by d Co
bcos a 17" CRT is veri much supported by a 600VA UPS [provided d ratings r authentic]
|
|
|
25-08-2007, 06:16 PM
|
#21 (permalink)
|
|
Right Off the Assembly Line
Join Date: Aug 2006
Posts: 7
|
If the change of the UPS doesn't work, I have to-have to change the monitor
|
|
|
25-08-2007, 07:40 PM
|
#22 (permalink)
|
|
Wise Old Owl
Join Date: Mar 2005
Location: shhhh!!!!! on a sniper point
Posts: 4,200
|
Re: Power Problem, suggest me please...
I suggest you to get an 800VA normal or online UPS. In that case there wud be no problem even if u add a G card, HDD, optical drive, printer, or speakers.
There wud be problem with an 500VA at powercuts only at times of load like gaming
or some animation worx
__________________
G1: PII X4 B50 4.0 | TRUE 120*2 | TA790GXB A2+ | 4GB DDR2 GSkill 1200 | Audigy 2 | HD4870 | HEC 550 | MX 518.
G2: AII 240 | M2N 68AM+ | 3GB| 8800GT | Zebby Plat 500
G3: XPS M1530 |
FZ 16.
|
|
|
25-08-2007, 08:06 PM
|
#23 (permalink)
|
|
ToTheBeatOfUrHeart
Join Date: Feb 2006
Location: Boston,Newyork
Posts: 1,882
|
Re: Power Problem, suggest me please...
I have APC 650 VA and APC is one of the best in maintaining constant current and voltage.And please check the rig it supports(my sig)
__________________
Mobo - P5N32-E SLI,P5N-E SLI|GFX - 2x8800GTS,8800GT|Processor - E6550,E6600|PSU - CM EP 600,HX620W|Physics - 2x8600GT
|
|
|
25-08-2007, 08:17 PM
|
#24 (permalink)
|
|
Wise Old Owl
Join Date: Mar 2005
Location: shhhh!!!!! on a sniper point
Posts: 4,200
|
Re: Power Problem, suggest me please...
@Harvik780
Yes, APC is surely a gud brand. But yours is a 650VA version and uve got 19" wide LCD which goes max upto 33w but a 19" flat CRT cud go upto 120w.
C2D, DDR2, etc consumes far less power than P4,DDR.
And what if he buy an 500VA one any it cudn't support the load??
So he should get at least an APC 650VA or better orelse he'wd have to change his monitor also and the total cost wud be a bomb.
__________________
G1: PII X4 B50 4.0 | TRUE 120*2 | TA790GXB A2+ | 4GB DDR2 GSkill 1200 | Audigy 2 | HD4870 | HEC 550 | MX 518.
G2: AII 240 | M2N 68AM+ | 3GB| 8800GT | Zebby Plat 500
G3: XPS M1530 |
FZ 16.
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
|
|