Old 09-05-2011, 03:22 PM   #1 (permalink)
Wise Old Owl
 
ithehappy's Avatar
 
Join Date: Sep 2010
Location: Uttarpara
Posts: 1,640
Default APC Black UPS making continuous Click sound on Power Failure !


Its the Black 1.1 KVA one. When power failure occurs it's making continuous Click sound till the power restores. I don't know if I am clear with the word click, but it's the same small click sound when you turn on the board switch where the UPS is plugged, not the UPS switch. Also an Amber colored light is blinking with every click sound from the replace battery light signal, the light is fade though. The Green On Line light is steady however. I have inverter installed, so when power failure happens the UPS runs on Inverter back up. Is that the reason of this weird sound? Is it harmful for the UPS? One more thing, with every Click sound the light of my room also blinks.

Please help me outta this. I don't like this sound at all. I am getting scared.

Thanks in advance.
__________________
i7 950SABERTOOTH8GB RAMGTX560690II +TX650

SGS II
ithehappy is offline   Reply With Quote
Advertisements. Register and be a member of the community to get rid of them.
Advertisement

Old 09-05-2011, 03:42 PM   #2 (permalink)
Uhu, Not Gonna Happen!
 
gagan007's Avatar
 
Join Date: Nov 2005
Location: Bangalore
Posts: 1,160
Default Re: APC Black UPS making continuous Click sound on Power Failure !

This click sound comes when the UPS tried to stabilize the voltage. It is normal sound when you use voltage stabilizers too (for refrigerators generally). Don't worry it is working fine.
__________________
My personal blog - http://gagan.scholarguru.com
gagan007 is offline   Reply With Quote
Old 09-05-2011, 06:09 PM   #3 (permalink)
RAMPAGE!!!!
 
modder's Avatar
 
Join Date: Oct 2010
Location: In my turtleneck!!!
Posts: 219
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Hey ithehapp, please go through this (try each setting, low volt. sensitivity/etc):

Voltage Sensitivity Adjustment
http://www.apcmedia.com/salestools/J...FB56_R0_EN.pdf

But I think the inverter is behind this. If you can, post the specs for the inverter especially voltage/output freq., sq. wave/modified sq. wave/sine wave/etc.

Is this 'tick-tick' happening only when running on inverter input?
modder is offline   Reply With Quote
Old 09-05-2011, 06:22 PM   #4 (permalink)
What The.... !!!
 
funkysourav's Avatar
 
Join Date: Jan 2009
Posts: 825
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Modder is spot on
i think when the power failure occurs, you get your backup power from inverter right?
APC UPSes are designed to only accept Sine Wave Power, when the Inverter tries to feed it Digital/Simulated sine wave power, it tries to uplink the power to a sine wave and thus the continuous clicking/chugging sound

Dont worry its a known issue with APC UPS and Non SineWave input power
if possible, disconnect UPS from Inverter as soon as Power Failure
or create a Raw Power Line from the mains which isn't connected to the Inverter
funkysourav is offline   Reply With Quote
Old 09-05-2011, 08:23 PM   #5 (permalink)
Wise Old Owl
 
ithehappy's Avatar
 
Join Date: Sep 2010
Location: Uttarpara
Posts: 1,640
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Quote:
Originally Posted by gagan007 View Post
This click sound comes when the UPS tried to stabilize the voltage. It is normal sound when you use voltage stabilizers too (for refrigerators generally). Don't worry it is working fine.
Thanks mate.
Quote:
Originally Posted by modder View Post
But I think the inverter is behind this. If you can, post the specs for the inverter especially voltage/output freq., sq. wave/modified sq. wave/sine wave/etc.

Is this 'tick-tick' happening only when running on inverter input?
Yes, only when running on inverter input.
Quote:
Originally Posted by funkysourav View Post
Modder is spot on
i think when the power failure occurs, you get your backup power from inverter right?
APC UPSes are designed to only accept Sine Wave Power, when the Inverter tries to feed it Digital/Simulated sine wave power, it tries to uplink the power to a sine wave and thus the continuous clicking/chugging sound

Dont worry its a known issue with APC UPS and Non SineWave input power
if possible, disconnect UPS from Inverter as soon as Power Failure
or create a Raw Power Line from the mains which isn't connected to the Inverter
Yea, right. It's not possible for me to disconnect the inverter to PC line. But I think from now on I will turn the UPS board switch OFF and let it run at it's Backup, in that way I don't have to hear that weird sound at least.

Thanks for your responses guys.
__________________
i7 950SABERTOOTH8GB RAMGTX560690II +TX650

SGS II
ithehappy is offline   Reply With Quote
Old 09-05-2011, 08:46 PM   #6 (permalink)
Super Moderator
 
asingh's Avatar
 
Join Date: May 2008
Location: New Delhi
Posts: 5,547
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Try not to run the UPS of the inverter. You will mess it up. The click click are the relays inside the UPS.
__________________
MSI P45 Platinum(BIOS v1.7B)|Q9550[E0]@3.85Ghz@1.320V[453x8.5]MCH@1.184V|ICH@1.55V|DDR_V_Ref_A_B@1.05V|NH-D14|Corsair TWIN2X4096-8500C5(5-5-5-15)@1089Mhz@2.14V
2xHD4890[Xfire]@1000/900[MEM/GPU]|Corsair 650TX|Seagate180GB+80GB+WD1TB|SONY-DVD-R|CM690|2x120mm Scythe Ultra Kaze|DELL S2409W|APC 1100VA|Scythe Kaze Server
Windows 7 Ultimate RTM - 64BIT|Catalyst 10.5 (8.14.10.0753) forced with RadeonPRO|PS3 160GB|Sony 40EX520|AC Ryan POHD Mini|APC 800VA|APC 800VA|D425KT|CM100 Elite|2TB WD|Acer D255

Test your spoiler tags before submitting
asingh is online now   Reply With Quote
Old 09-05-2011, 09:19 PM   #7 (permalink)
RAMPAGE!!!!
 
modder's Avatar
 
Join Date: Oct 2010
Location: In my turtleneck!!!
Posts: 219
Default Re: APC Black UPS making continuous Click sound on Power Failure !

@ithehappy
you should seriously consider this, even if its not possible :

Quote:
Originally Posted by funkysourav
create a Raw Power Line from the mains which isn't connected to the Inverter
modder is offline   Reply With Quote
Old 10-05-2011, 06:52 PM   #8 (permalink)
Wise Old Owl
 
ithehappy's Avatar
 
Join Date: Sep 2010
Location: Uttarpara
Posts: 1,640
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Yea guys. But it's not possible for me to create a raw line from main. But I've decided that I'll let the UPS to go to Backup mode when Power failure will occur, then I'll turn the PC off. That's better I guess. There will be no problem if everything is OFF

BTW- The Battery is Exide 800W one with Luminous inverter. I'll try to upload the specs if I find it.

Today a strange thing happened. Power failed, again, I instantly turned off the UPS board switch to let it work in Backup mode and also to don't let my inverter to control the PC and UPS but after 5-6 seconds while PC got turned off with continuous beep sound from the UPS, which I guess is the low battery sound warning. I haven't used any Backup from my UPS which could cause discharge of battery. Now I am giving it a 6 hours charge again. Lets see what happens next, BUT today's incident was definitely weird.
__________________
i7 950SABERTOOTH8GB RAMGTX560690II +TX650

SGS II
ithehappy is offline   Reply With Quote
Old 16-11-2011, 09:12 PM   #9 (permalink)
Right Off the Assembly Line
 
Join Date: Nov 2011
Posts: 2
Default Re: APC Black UPS making continuous Click sound on Power Failure !

I got the same problem too ! !

I have a computer with APC 1.1KV UPS

And i recently bought an inverter to backup my computer too

The inverter is LUMINOUS SineWave 1.5 KV model.


Whenever the current swithes to inverter my UPS stars tiking as U said !
And the UPS SHUTS DOWN when it looses its BAKUP !


This is really annoying !
I was advised to connnect my Computer without the UPS.
And it works well that way.

But I am still worried about why this is happening.
I feel Luminous SineWave isn't good enough 4 the UPS !

How do I find that ?

Last edited by kingofleo; 19-11-2011 at 09:01 PM.
kingofleo is offline   Reply With Quote
Old 16-11-2011, 11:34 PM   #10 (permalink)
BMG ftw!!
 
d6bmg's Avatar
 
Join Date: Aug 2011
Location: Kolkata
Posts: 3,806
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Quote:
Originally Posted by kingofleo View Post
Spoiler:
I got the same problem too ! !

I have a computer with APC 1.1KV UPS

And i recently bought an inverter to backup my computer too

The inverter is LUMINOUS SineWave 1.5 KV model.


Whenever the current swithes to inverter my UPS stars tiking as U said !
And the UPS SHUTS DOWN when it looses its BAKUP !


This is really annoying !
I was advised to connnect my Computer directly to the power source.
And it works well that way.

But I am still worried about why this is happening.
I feel Luminous SineWave isn't good enough 4 the UPS !

How do I find that ?
One request. Please don't bump like this in any old thread. Create a new thread for your problem.


@admin: this is not the first time I'm seeing this today. In another thread, Tenida posted same message which I'm doing now in this thread. So, an auto-locking feature would be of great help.
d6bmg is offline   Reply With Quote
Old 19-11-2011, 08:15 PM   #11 (permalink)
Right Off the Assembly Line
 
Join Date: Nov 2011
Posts: 2
Default Re: APC Black UPS making continuous Click sound on Power Failure !

@d6bmp: actually i don't want to bump on this post.

so u better read my post well.

I post this here because my problem was exactly identical, and I am close to finding a solution.
And thus could find a solution to this thread overall.

The Problem is Between Luminious Inverter(SineWave) and an APC UPS.

Need to find whats wrong.
My latest finding is that Luminous Sinewave is not good sine wave for the UPS.

They say its a Digital Sine wave unlike, the Pure SineWave that APC Inverters ! !

Last edited by kingofleo; 19-11-2011 at 11:21 PM.
kingofleo is offline   Reply With Quote
Old 17-05-2012, 11:13 PM   #12 (permalink)
Right Off the Assembly Line
 
Join Date: May 2012
Posts: 5
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Quote:
Originally Posted by kingofleo View Post
@d6bmp: actually i don't want to bump on this post.

so u better read my post well.

I post this here because my problem was exactly identical, and I am close to finding a solution.
And thus could find a solution to this thread overall.

The Problem is Between Luminious Inverter(SineWave) and an APC UPS.

Need to find whats wrong.
My latest finding is that Luminous Sinewave is not good sine wave for the UPS.

They say its a Digital Sine wave unlike, the Pure SineWave that APC Inverters ! !

I am having this same problem with my Sukam inverter ( also called Home ups ) and Microtek UPS . what can I do , it seems that the cycles are not matching, I cannot connect PC directly to Inverter because PC reboots, when Inverter goes into Back up mode.Please help

Last edited by Tech123; 18-05-2012 at 04:36 AM.
Tech123 is offline   Reply With Quote
Old 18-05-2012, 02:42 PM   #13 (permalink)
*
 
bajaj151's Avatar
 
Join Date: May 2006
Location: India
Posts: 865
Default Re: APC Black UPS making continuous Click sound on Power Failure !

I have Microtek 850EB Inverter..When I directly connect the PC with Inverter, PC does not reboot when power goes off...

But afaik..it's not safe to connect directly to inverter..That's why I am using UPS in between...But now after adding graphics card, UPS can't able to take load.

Now, I am searching new UPS for my system.
APC ups do have problems when connected to inverter....
__________________
Phenom x6 1055T 3.75 GHz | MSI 890GXM G65 | Corsair XMS3 2*4GB 1600mhz | BenQ E2200HD | Xbox 360 Controller | Seagate 2TB | CM HAF 922 | Corsair VX 550 | Logitech MX 518 | Logitech Wireless Keyboard | Sapphire 7850 OC

Last edited by bajaj151; 20-05-2012 at 01:58 PM. Reason: Added model no.
bajaj151 is offline   Reply With Quote
Old 20-05-2012, 02:08 AM   #14 (permalink)
Right Off the Assembly Line
 
Join Date: May 2012
Posts: 5
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Hi bajaj Please mention your mictotek model and tell me if there is a switch at the back by which you can select the working voltage range,
Tech123 is offline   Reply With Quote
Old 20-05-2012, 02:00 PM   #15 (permalink)
*
 
bajaj151's Avatar
 
Join Date: May 2006
Location: India
Posts: 865
Default Re: APC Black UPS making continuous Click sound on Power Failure !

Microtek 850EB

Yes, there is a switch at the back..



Asked Microtek (via email) regarding the same.
And they replied : You can connect computer directly with Inverter but input range shall then be selected on 180-260v range....
__________________
Phenom x6 1055T 3.75 GHz | MSI 890GXM G65 | Corsair XMS3 2*4GB 1600mhz | BenQ E2200HD | Xbox 360 Controller | Seagate 2TB | CM HAF 922 | Corsair VX 550 | Logitech MX 518 | Logitech Wireless Keyboard | Sapphire 7850 OC

Last edited by bajaj151; 20-05-2012 at 05:28 PM.
bajaj151 is offline   Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


 
Latest Threads
- by trublu
- by Sujeet
- by ico
- by Tenida
- by c4u

Advertisement




All times are GMT +5.5. The time now is 03:35 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.

Search Engine Optimization by vBSEO 3.3.2