09-05-2011, 03:22 PM
|
#1 (permalink)
|
|
Wise Old Owl
Join Date: Sep 2010
Location: Uttarpara
Posts: 1,640
|
APC Black UPS making continuous Click sound on Power Failure !
Its the Black 1.1 KVA one. When power failure occurs it's making continuous Click sound till the power restores. I don't know if I am clear with the word click, but it's the same small click sound when you turn on the board switch where the UPS is plugged, not the UPS switch. Also an Amber colored light is blinking with every click sound from the replace battery light signal, the light is fade though. The Green On Line light is steady however. I have inverter installed, so when power failure happens the UPS runs on Inverter back up. Is that the reason of this weird sound? Is it harmful for the UPS? One more thing, with every Click sound the light of my room also blinks.
Please help me outta this. I don't like this sound at all. I am getting scared.
Thanks in advance.
__________________
i7 950►SABERTOOTH►8GB RAM►GTX560►690II +►TX650
SGS II
|
|
|
|
Advertisements. Register and be a member of the community to get rid of them.
|
|
Advertisement
|
|
09-05-2011, 03:42 PM
|
#2 (permalink)
|
|
Uhu, Not Gonna Happen!
Join Date: Nov 2005
Location: Bangalore
Posts: 1,160
|
Re: APC Black UPS making continuous Click sound on Power Failure !
This click sound comes when the UPS tried to stabilize the voltage. It is normal sound when you use voltage stabilizers too (for refrigerators generally). Don't worry it is working fine.
__________________
My personal blog - http://gagan.scholarguru.com
|
|
|
09-05-2011, 06:09 PM
|
#3 (permalink)
|
|
RAMPAGE!!!!
Join Date: Oct 2010
Location: In my turtleneck!!!
Posts: 219
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Hey ithehapp, please go through this (try each setting, low volt. sensitivity/etc):
Voltage Sensitivity Adjustment
http://www.apcmedia.com/salestools/J...FB56_R0_EN.pdf
But I think the inverter is behind this. If you can, post the specs for the inverter especially voltage/output freq., sq. wave/modified sq. wave/sine wave/etc.
Is this 'tick-tick' happening only when running on inverter input?
|
|
|
09-05-2011, 06:22 PM
|
#4 (permalink)
|
|
What The.... !!!
Join Date: Jan 2009
Posts: 825
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Modder is spot on
i think when the power failure occurs, you get your backup power from inverter right?
APC UPSes are designed to only accept Sine Wave Power, when the Inverter tries to feed it Digital/Simulated sine wave power, it tries to uplink the power to a sine wave and thus the continuous clicking/chugging sound
Dont worry its a known issue with APC UPS and Non SineWave input power
if possible, disconnect UPS from Inverter as soon as Power Failure
or create a Raw Power Line from the mains which isn't connected to the Inverter
|
|
|
09-05-2011, 08:23 PM
|
#5 (permalink)
|
|
Wise Old Owl
Join Date: Sep 2010
Location: Uttarpara
Posts: 1,640
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Quote:
Originally Posted by gagan007
This click sound comes when the UPS tried to stabilize the voltage. It is normal sound when you use voltage stabilizers too (for refrigerators generally). Don't worry it is working fine.
|
Thanks mate.
Quote:
Originally Posted by modder
But I think the inverter is behind this. If you can, post the specs for the inverter especially voltage/output freq., sq. wave/modified sq. wave/sine wave/etc.
Is this 'tick-tick' happening only when running on inverter input?
|
Yes, only when running on inverter input.
Quote:
Originally Posted by funkysourav
Modder is spot on
i think when the power failure occurs, you get your backup power from inverter right?
APC UPSes are designed to only accept Sine Wave Power, when the Inverter tries to feed it Digital/Simulated sine wave power, it tries to uplink the power to a sine wave and thus the continuous clicking/chugging sound
Dont worry its a known issue with APC UPS and Non SineWave input power
if possible, disconnect UPS from Inverter as soon as Power Failure
or create a Raw Power Line from the mains which isn't connected to the Inverter
|
Yea, right. It's not possible for me to disconnect the inverter to PC line. But I think from now on I will turn the UPS board switch OFF and let it run at it's Backup, in that way I don't have to hear that weird sound at least.
Thanks for your responses guys.
__________________
i7 950►SABERTOOTH►8GB RAM►GTX560►690II +►TX650
SGS II
|
|
|
09-05-2011, 08:46 PM
|
#6 (permalink)
|
|
Super Moderator
Join Date: May 2008
Location: New Delhi
Posts: 5,547
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Try not to run the UPS of the inverter. You will mess it up. The click click are the relays inside the UPS.
__________________
MSI P45 Platinum(BIOS v1.7B)|Q9550[E0]@3.85Ghz@1.320V[453x8.5]MCH@1.184V|ICH@1.55V|DDR_V_Ref_A_B@1.05V|NH-D14|Corsair TWIN2X4096-8500C5(5-5-5-15)@1089Mhz@2.14V
2xHD4890[Xfire]@1000/900[MEM/GPU]|Corsair 650TX|Seagate180GB+80GB+WD1TB|SONY-DVD-R|CM690|2x120mm Scythe Ultra Kaze|DELL S2409W|APC 1100VA|Scythe Kaze Server
Windows 7 Ultimate RTM - 64BIT|Catalyst 10.5 (8.14.10.0753) forced with RadeonPRO|PS3 160GB|Sony 40EX520|AC Ryan POHD Mini|APC 800VA|APC 800VA|D425KT|CM100 Elite|2TB WD|Acer D255
Test your spoiler tags before submitting
|
|
|
09-05-2011, 09:19 PM
|
#7 (permalink)
|
|
RAMPAGE!!!!
Join Date: Oct 2010
Location: In my turtleneck!!!
Posts: 219
|
Re: APC Black UPS making continuous Click sound on Power Failure !
@ithehappy
you should seriously consider this, even if its not possible  :
Quote:
|
Originally Posted by funkysourav
create a Raw Power Line from the mains which isn't connected to the Inverter
|
|
|
|
10-05-2011, 06:52 PM
|
#8 (permalink)
|
|
Wise Old Owl
Join Date: Sep 2010
Location: Uttarpara
Posts: 1,640
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Yea guys. But it's not possible for me to create a raw line from main. But I've decided that I'll let the UPS to go to Backup mode when Power failure will occur, then I'll turn the PC off. That's better I guess. There will be no problem if everything is OFF
BTW- The Battery is Exide 800W one with Luminous inverter. I'll try to upload the specs if I find it.
Today a strange thing happened. Power failed, again, I instantly turned off the UPS board switch to let it work in Backup mode and also to don't let my inverter to control the PC and UPS but after 5-6 seconds while PC got turned off with continuous beep sound from the UPS, which I guess is the low battery sound warning. I haven't used any Backup from my UPS which could cause discharge of battery. Now I am giving it a 6 hours charge again. Lets see what happens next, BUT today's incident was definitely weird.
__________________
i7 950►SABERTOOTH►8GB RAM►GTX560►690II +►TX650
SGS II
|
|
|
16-11-2011, 09:12 PM
|
#9 (permalink)
|
|
Right Off the Assembly Line
Join Date: Nov 2011
Posts: 2
|
Re: APC Black UPS making continuous Click sound on Power Failure !
I got the same problem too ! !
I have a computer with APC 1.1KV UPS
And i recently bought an inverter to backup my computer too
The inverter is LUMINOUS SineWave 1.5 KV model.
Whenever the current swithes to inverter my UPS stars tiking as U said !
And the UPS SHUTS DOWN when it looses its BAKUP !
This is really annoying !
I was advised to connnect my Computer without the UPS.
And it works well that way.
But I am still worried about why this is happening.
I feel Luminous SineWave isn't good enough 4 the UPS !
How do I find that ?
Last edited by kingofleo; 19-11-2011 at 09:01 PM.
|
|
|
16-11-2011, 11:34 PM
|
#10 (permalink)
|
|
BMG ftw!!
Join Date: Aug 2011
Location: Kolkata
Posts: 3,806
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Quote:
Originally Posted by kingofleo
|
One request. Please don't bump like this in any old thread. Create a new thread for your problem.
@admin: this is not the first time I'm seeing this today. In another thread, Tenida posted same message which I'm doing now in this thread. So, an auto-locking feature would be of great help.
|
|
|
19-11-2011, 08:15 PM
|
#11 (permalink)
|
|
Right Off the Assembly Line
Join Date: Nov 2011
Posts: 2
|
Re: APC Black UPS making continuous Click sound on Power Failure !
@d6bmp: actually i don't want to bump on this post.
so u better read my post well.
I post this here because my problem was exactly identical, and I am close to finding a solution.
And thus could find a solution to this thread overall.
The Problem is Between Luminious Inverter(SineWave) and an APC UPS.
Need to find whats wrong.
My latest finding is that Luminous Sinewave is not good sine wave for the UPS.
They say its a Digital Sine wave unlike, the Pure SineWave that APC Inverters ! !
Last edited by kingofleo; 19-11-2011 at 11:21 PM.
|
|
|
17-05-2012, 11:13 PM
|
#12 (permalink)
|
|
Right Off the Assembly Line
Join Date: May 2012
Posts: 5
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Quote:
Originally Posted by kingofleo
@d6bmp: actually i don't want to bump on this post.
so u better read my post well.
I post this here because my problem was exactly identical, and I am close to finding a solution.
And thus could find a solution to this thread overall.
The Problem is Between Luminious Inverter(SineWave) and an APC UPS.
Need to find whats wrong.
My latest finding is that Luminous Sinewave is not good sine wave for the UPS.
They say its a Digital Sine wave unlike, the Pure SineWave that APC Inverters ! !
|
I am having this same problem with my Sukam inverter ( also called Home ups ) and Microtek UPS . what can I do , it seems that the cycles are not matching, I cannot connect PC directly to Inverter because PC reboots, when Inverter goes into Back up mode.Please help
Last edited by Tech123; 18-05-2012 at 04:36 AM.
|
|
|
18-05-2012, 02:42 PM
|
#13 (permalink)
|
|
*
Join Date: May 2006
Location: India
Posts: 865
|
Re: APC Black UPS making continuous Click sound on Power Failure !
I have Microtek 850EB Inverter..When I directly connect the PC with Inverter, PC does not reboot when power goes off...
But afaik..it's not safe to connect directly to inverter..That's why I am using UPS in between...But now after adding graphics card, UPS can't able to take load.
Now, I am searching new UPS for my system.
APC ups do have problems when connected to inverter....
__________________
Phenom x6 1055T 3.75 GHz | MSI 890GXM G65 | Corsair XMS3 2*4GB 1600mhz | BenQ E2200HD | Xbox 360 Controller | Seagate 2TB | CM HAF 922 | Corsair VX 550 | Logitech MX 518 | Logitech Wireless Keyboard | Sapphire 7850 OC
Last edited by bajaj151; 20-05-2012 at 01:58 PM.
Reason: Added model no.
|
|
|
20-05-2012, 02:08 AM
|
#14 (permalink)
|
|
Right Off the Assembly Line
Join Date: May 2012
Posts: 5
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Hi bajaj Please mention your mictotek model and tell me if there is a switch at the back by which you can select the working voltage range,
|
|
|
20-05-2012, 02:00 PM
|
#15 (permalink)
|
|
*
Join Date: May 2006
Location: India
Posts: 865
|
Re: APC Black UPS making continuous Click sound on Power Failure !
Microtek 850EB
Yes, there is a switch at the back..
Asked Microtek (via email) regarding the same.
And they replied : You can connect computer directly with Inverter but input range shall then be selected on 180-260v range....
__________________
Phenom x6 1055T 3.75 GHz | MSI 890GXM G65 | Corsair XMS3 2*4GB 1600mhz | BenQ E2200HD | Xbox 360 Controller | Seagate 2TB | CM HAF 922 | Corsair VX 550 | Logitech MX 518 | Logitech Wireless Keyboard | Sapphire 7850 OC
Last edited by bajaj151; 20-05-2012 at 05:28 PM.
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
|
|